Any electricians here? Nearly had electrical fire yesterday (1 Viewer)

matttyl

Footballguy
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
 
I mean, I get wanting to come here and ask and I get you have some knowledge of this.

But this is an immediate call to an electrician to diagnose and remedy this situation, IMO. There is zero chance I would risk burning my family home down after this incident without someone licensed and trained no matter what I read or thought I knew. Not the time to save a few bucks.

Glad to hear everyone is ok.
 
I mean, I get wanting to come here and ask and I get you have some knowledge of this.

But this is an immediate call to an electrician to diagnose and remedy this situation, IMO. There is zero chance I would risk burning my family home down after this incident without someone licensed and trained no matter what I read or thought I knew. Not the time to save a few bucks.

Glad to hear everyone is ok.

Agreed, and making those calls this morning to get someone out, but it could be a few days before they can come.
 
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
If the dryer was electric that plug is 220. So the answer is NO unless you change the breaker to a normal breaker.

You could then theoretically change that dryer outlet to a normal outlet, but you would want to make sure you wire it correctly.

It would need to be wired properly in the breaker box as well. Remember, those 220's are wired with two hots. You do not want to screw this up
 
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
If the dryer was electric that plug is 220. So the answer is NO unless you change the breaker to a normal breaker.

You could then theoretically change that dryer outlet to a normal outlet, but you would want to make sure you wire it correctly.

It would need to be wired properly in the breaker box as well. Remember, those 220's are wired with two hots. You do not want to screw this up

Yes, I read about doing that, and that’s definitely a job I’d hire out for. You change the breaker to a dual pole 15amp and then wire two dual outlets - but all that is just a bit beyond my DIY ability and comfort level.

That outlet is a 220, bit isn’t the adapter changing that to 110?

 
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
You mean like this?

If so then yes, you would be good to go. I would have an electrician check out the wire where the other melted down just to be sure it can be be used again
 
Adapter
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
You mean like this?

If so then yes, you would be good to go. I would have an electrician check out the wire where the other melted down just to be sure it can be be used again

Very similar to that, but the one with a “box” at the end with 4 plugs and a built in circuit breaker. I tried to link to it above, but unsure how to properly link to a site via my phone.
 
Adapter
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
You mean like this?

If so then yes, you would be good to go. I would have an electrician check out the wire where the other melted down just to be sure it can be be used again

Very similar to that, but the one with a “box” at the end with 4 plugs and a built in circuit breaker. I tried to link to it above, but unsure how to properly link to a site via my phone.
Yeah, I saw your post after I posted.
Also, running a new wire to a new outlet yourself isn’t that big of a deal and would save you some $$
 
Yeah - I do a lot of electrical stuff myself, but the second you start messing or considering 220v, and especially if you have an overloaded line that melted an outlet, I'd rely on a pro. I totally get what you're doing, but I'd have concerns over potential damage to the original line. If it got hot enough to melt the outlet, it may have caused issues elsewhere.

For your short-term fix, I'd just keep the essential stuff on that circuit, and either avoid using the others or plug them in elsewhere. Probably leave your well pump as-is, and maybe the fridge if that's been fine in the past, and run the dehumidifier off another outlet or an extension cord, and just don't vacuum for a few days.
 
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
So, you have water and your freezer's working now (sorry, my reading comprehension is going backwards through puberty)? If so, I'd wait for a pro to come out and fix it as long as it doesn't keep throwing the circuit.

I'd also have them balance your panel if needed and you have room.
 
Adapter
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
You mean like this?

If so then yes, you would be good to go. I would have an electrician check out the wire where the other melted down just to be sure it can be be used again

Very similar to that, but the one with a “box” at the end with 4 plugs and a built in circuit breaker. I tried to link to it above, but unsure how to properly link to a site via my phone.
Yeah, I saw your post after I posted.
Also, running a new wire to a new outlet yourself isn’t that big of a deal and would save you some $$

If it weren’t all behind drywall, I would. Much of this was the doing of the prior owner when he finished the basement for an in law suite (hence the currently unused dryer socket).
 
Last edited:
Just my 2 cents of advice, I would log onto to the Next Door app and search around on there for recommended licensed electricians. I did this, years and years ago and the guy I use is amazing, he's inexpensive, he's intelligent, he's quick and he does an outstanding job. I had him overlook my work, he found mistakes, fixed the mistakes and explained what I did wrong and why. And then make sure you get working smoke detectors, which I know sounds elementary but until you get that inspected by a licensed electrician, I would be extremely vigilant right now.
 
Adapter
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
You mean like this?

If so then yes, you would be good to go. I would have an electrician check out the wire where the other melted down just to be sure it can be be used again

Very similar to that, but the one with a “box” at the end with 4 plugs and a built in circuit breaker. I tried to link to it above, but unsure how to properly link to a site via my phone.
Yeah, I saw your post after I posted.
Also, running a new wire to a new outlet yourself isn’t that big of a deal and would save you some $$

If it weren’t all behind drywall, I would. Much of this was the doing of the prior owner when he finished the basement for an in law suite (hence the currently unused dryer socket).
I gotcha. I read partially finished so wasn’t sure
 
Got an electrician scheduled later this week to go over everything and make sure history doesn’t repeat!
Get the freezer off the GFI. You don't want to have a gfi trip unknowingly and lose your food.

Doesn’t a gfci tripping only impact that socket and everything “downstream) from it? The gfci is “after” where the freezer is plugged in on this circuit.
Reading Is Fundamental :bag:
 
@matttyl It sounds to me like you may have had loose connections at that outlet causing arcing, especially with slight movement like plugging in the vacuum and tester. An overload situation would generally trip the breaker, not cause a fire, unless the breaker itself has failed but they normally fail open...
 
@matttyl It sounds to me like you may have had loose connections at that outlet causing arcing, especially with slight movement like plugging in the vacuum and tester. An overload situation would generally trip the breaker, not cause a fire, unless the breaker itself has failed but they normally fail open...

Yeah, I think k your right as the “pop” happened when I plugged in the tester - and that’s also when the breaker tripped - so I know that works. Outlet has been replaced with a heavier duty 15 amp. Should get the all good from electrician later this week.

Did confirm that the wire between 2nd to last and the last plug on the circuit is in fact 14 gauge wire and not 12 gauge, but it’s the only part of that circuit in non finished space so it can be replaced easily. Apparently mixing wire size, even for the last socket, is a no no.
 
Yeah, I think k your right as the “pop” happened when I plugged in the tester - and that’s also when the breaker tripped - so I know that works. Outlet has been replaced with a heavier duty 15 amp. Should get the all good from electrician later this week.

Did confirm that the wire between 2nd to last and the last plug on the circuit is in fact 14 gauge wire and not 12 gauge, but it’s the only part of that circuit in non finished space so it can be replaced easily. Apparently mixing wire size, even for the last socket, is a no no.
The whole circuit is a no-no.

So, on a 20A breaker, everything that follows it needs to be capable of 20A.

You need 12/2 wire and 20A sockets.

By you changing to a 15A breaker, you should be ok on that line of 4 sockets. EXCEPT, the well pump.

If you have an open spot in your panel, I'm putting that one on it's own circuit. No way I'm having a freezer and well pump on the same 15A circuit.
 
Yeah, I think k your right as the “pop” happened when I plugged in the tester - and that’s also when the breaker tripped - so I know that works. Outlet has been replaced with a heavier duty 15 amp. Should get the all good from electrician later this week.

Did confirm that the wire between 2nd to last and the last plug on the circuit is in fact 14 gauge wire and not 12 gauge, but it’s the only part of that circuit in non finished space so it can be replaced easily. Apparently mixing wire size, even for the last socket, is a no no.
The whole circuit is a no-no.

So, on a 20A breaker, everything that follows it needs to be capable of 20A.

You need 12/2 wire and 20A sockets.

By you changing to a 15A breaker, you should be ok on that line of 4 sockets. EXCEPT, the well pump.

If you have an open spot in your panel, I'm putting that one on it's own circuit. No way I'm having a freezer and well pump on the same 15A circuit.

From my reading (and YouTube) that’s not correct. On a 20 amp circuit, if it’s the only plug on that circuit, it must be a 20 amp outlet. If you’re using multiple outlets on that circuit, as I am, with a 20 amp breaker, you must use 12 gauge wire, but also can (or must?) use 15 amp outlets.
 
Yeah, I think k your right as the “pop” happened when I plugged in the tester - and that’s also when the breaker tripped - so I know that works. Outlet has been replaced with a heavier duty 15 amp. Should get the all good from electrician later this week.

Did confirm that the wire between 2nd to last and the last plug on the circuit is in fact 14 gauge wire and not 12 gauge, but it’s the only part of that circuit in non finished space so it can be replaced easily. Apparently mixing wire size, even for the last socket, is a no no.
The whole circuit is a no-no.

So, on a 20A breaker, everything that follows it needs to be capable of 20A.

You need 12/2 wire and 20A sockets.

By you changing to a 15A breaker, you should be ok on that line of 4 sockets. EXCEPT, the well pump.

If you have an open spot in your panel, I'm putting that one on it's own circuit. No way I'm having a freezer and well pump on the same 15A circuit.

From my reading (and YouTube) that’s not correct. On a 20 amp circuit, if it’s the only plug on that circuit, it must be a 20 amp outlet. If you’re using multiple outlets on that circuit, as I am, with a 20 amp breaker, you must use 12 gauge wire, but also can (or must?) use 15 amp outlets.
You may be right. It's been a long time since I was a licensed contractor.

But I wouldn't do that in my house.
 
Yeah, I think k your right as the “pop” happened when I plugged in the tester - and that’s also when the breaker tripped - so I know that works. Outlet has been replaced with a heavier duty 15 amp. Should get the all good from electrician later this week.

Did confirm that the wire between 2nd to last and the last plug on the circuit is in fact 14 gauge wire and not 12 gauge, but it’s the only part of that circuit in non finished space so it can be replaced easily. Apparently mixing wire size, even for the last socket, is a no no.
The whole circuit is a no-no.

So, on a 20A breaker, everything that follows it needs to be capable of 20A.

You need 12/2 wire and 20A sockets.

By you changing to a 15A breaker, you should be ok on that line of 4 sockets. EXCEPT, the well pump.

If you have an open spot in your panel, I'm putting that one on it's own circuit. No way I'm having a freezer and well pump on the same 15A circuit.

From my reading (and YouTube) that’s not correct. On a 20 amp circuit, if it’s the only plug on that circuit, it must be a 20 amp outlet. If you’re using multiple outlets on that circuit, as I am, with a 20 amp breaker, you must use 12 gauge wire, but also can (or must?) use 15 amp outlets.
You may be right. It's been a long time since I was a licensed contractor.

But I wouldn't do that in my house.

I get where you’re coming from. I think the idea is if you have the need for a 20 amp outlet, use a 20 amp outlet and have that be the only outlet on that circuit. If you have multiple outlets on the circuit, if they are all 20 amp plugs (which look different), one might be included to plug a freezer into one, a well pump into another, another high amp device in the third and another in the fourth and overload the circuit. Especially if it’s the next homeowner (like me) who didn’t know what was on each circuit until this happened.

Jet pump being put on its own circuit shortly. Freezer and dehumidifier and even a vacuum should all be fine on a 20 amp circuit.
 
So everyone is fine, no fire, but blew an outlet which after removing it was totally melted. I think I understand why, and also what to do to fix, just want to verify.

I learned all this yesterday, though have lived in house for 12 years now. I have a 20 amp circuit from breaker box to four and only four outlets in my mostly finished basement. The wire looks to be 12 awg from breaker box to the first 3, and then 14 to the final. The first outlet is a 15 amp regular wall socket, and it’s the one that melted. It has a small chest freezer plugged into it 24/7. The next in line is a gfci plug by a sink in the kitchenette, and is rarely used. The third is a regular 15 amp socket that during the summer has a dehumidifier plugged into and running. And the final socket on circuit is a 15 amp plug with our well/jet water pump - which I think is the main culprit here as when it starts up it can draw 12+ amps on its own. I don’t know if that’s higher than it been in the past as I only ever measured that yesterday, but seems reasonable from what I’ve read for the startup amps of a 1/2hp pump.

Anyway, yesterday my wife happened to plug in a vacuum to the plug with the dehumidifier and smelled something burning. We saw that the first outlet in the series had the smell and some black marks. I went and got my “plug tester” tool from garage, plugged it into that outlet, at which point the outlet literally blew up/melted, and thank goodness tripped the breaker. I then removed the outlet and discovered how bad it had melted, and started with my detective work.

After realizing that the freezer, dehumidifier and well pump are all on that circuit all the time, and a vacuum or similar could also be plugged into and used - that’s way too much amperage for the line, which is what blew the outlet.

So I replaced the outlet with a “heavy duty” but still 15 amp one from Home Depot. I read mixed information about replacing a 15a with a 20a outlet so decided to keep it the same. Moved the dehumidifier to a different outlet on a different circuit. That’s the short term fix and honestly should be enough if we remember not to plug in anything else.

Long term, though, I have an idea - hope this works and is safe. As luck would have it, there is an unused 14/30 outlet near where the well/jet pump is as there had previously been a dryer there. Since it’s not currently being used I’d turned off its breaker and forgotten about it. So I found a 14/30 to 15a plug adapter on Amazon (the one with a 1.5 foot cord and built in circuit breaker, looks like something for an RV). Can I plug that into the 14/30 outlet, flip that breaker back on, and plug just the jet pump into it to give that its own dedicated circuit? If so, the other circuit should now be able to handle the freezer, dehumidifier and even the occasionally vacuum from time to time without worrying about what gets plugged into where. Thoughts?

Oh, and happy belated Father’s Day! I had a great one working on home electoral stuff all day!
Since all outlets are daisy chained, it's possible that the first outlet (the one the burned) was used as a pass thru, and all current running to the outlets downstream pass through that first one. The right way to do this is to pigtail the hot and neutral to that outlet, so that it doesn't see the current flowing to the others. In fact, all other outlets should be done similarly if there are outlets downstream on the same breaker, i.e. all outlets are pigtailed, not pass-thru. That's an easy enough change as long as the box is deep enough to handle the pigtails.

Also, Wagos are better than wire nuts. Sooooo much better.
 